Kevin Squires, Sr. Project Coordinator – Day & Zimmermann (Condenser Services)
October 11, 2017 • Diplomat Resort and Spa • Hollywood, Florida, USA
ONE‐FOR‐ONE CONDENSER RETUBING
With Titanium Alloy Tubing
Kevin Squires, Sr. Project Coordinator – Day & Zimmermann (Condenser Services)
October 11, 2017 • Diplomat Resort and Spa • Hollywood, Florida, USA
Presentation Outline
• Considerations for Retubing• Why Retube with Titanium?• Titanium Tubing Requirements• Project Planning / Planning for “Murphy”• Vibration and Uplift Analyses
• Vibration Resolution• Uplift Consideration
• Pullout Testing• Serrations• Cathodic Protection Considerations• Steps for a Retubing
Successfully performing a condenser retubing with new titanium tubes requires advanced planning, extensive expertise in condenser design and operation, and superb project execution.
Kevin Squires, Sr. Project Coordinator – Day & Zimmermann (Condenser Services)
October 11, 2017 • Diplomat Resort and Spa • Hollywood, Florida, USA
Considerations for Retubing Your Condenser
10% or more of the total amount of tubes are either plugged and/or have failed
Severe wall loss
Existing tube material leaches out onto components (turbine, feedwater heaters, etc.) or deposits unacceptable chemicals into cooling water source, harmful to ecosystem
Kevin Squires, Sr. Project Coordinator – Day & Zimmermann (Condenser Services)
October 11, 2017 • Diplomat Resort and Spa • Hollywood, Florida, USA
Why Retube with Titanium?
Immune to:• Contaminants from cooling water
• Chloride attack• Under deposit pitting
Kevin Squires, Sr. Project Coordinator – Day & Zimmermann (Condenser Services)
October 11, 2017 • Diplomat Resort and Spa • Hollywood, Florida, USA
Why Retube with Titanium?
Improved Tooling & Field Processes Ensure:• Successful expansion of thin‐walled material• Enhanced tube‐to‐tubesheet joint strength• Vibration Resolution
Kevin Squires, Sr. Project Coordinator – Day & Zimmermann (Condenser Services)
October 11, 2017 • Diplomat Resort and Spa • Hollywood, Florida, USA
Project Planning
Considerations – when retubing with Titanium, include the following:
Pullout Test Tubesheet Serrations
Vibration & Uplift
Analyses
Tubesheet Replacement
Cathodic Protection Analysis
Coating Tubesheets & Waterboxes
Kevin Squires, Sr. Project Coordinator – Day & Zimmermann (Condenser Services)
October 11, 2017 • Diplomat Resort and Spa • Hollywood, Florida, USA
Project Planning
Project Duration – on average, most condenser retubingsrequire approximately 4 to 6 weeks to complete; however, the duration of the project depends upon many factors:
Number and length of tubes
Analyses to be performed
Presence of plugs, inserts, stakes, and/or
coating on tubesheets/waterboxes
Complexity / amount of interferences requiring
removalAccess to work area Anticipated major
repairs needed
Kevin Squires, Sr. Project Coordinator – Day & Zimmermann (Condenser Services)
October 11, 2017 • Diplomat Resort and Spa • Hollywood, Florida, USA
Project PlanningPreparation of Work Scope / RFQ:
Determine the scope of work and schedule/time available to perform retubing
Outline who will be responsible for providing what services, materials, tooling and equipment, etc., which should include (as a minimum):
Replacement tubes (lead times can be extensive)
Training / Backgrounds / Drug Testing
Interference Removal / Reinstallation
Scaffolding (provide, erect/adjust/dismantle)
Replacement nuts, bolts, gaskets, Circ water expansion joints
Lifting beam / off-loading /staging new tubes
On-site Utilities (electric, air,water)
On-site Facilities / LaydownAreas
Confined space program Overhead crane (if applicable) Lifting beam Scrap tube containers/disposal
Kevin Squires, Sr. Project Coordinator – Day & Zimmermann (Condenser Services)
October 11, 2017 • Diplomat Resort and Spa • Hollywood, Florida, USA
Project Planning
Preparation of Work Scope / RFQ:
Conduct pre-bid meeting and site walk down with all bidders present
Review bids, check references, and select contractor
Issue specification to qualified contractors at least 6-12 months before work is to be performed
Kevin Squires, Sr. Project Coordinator – Day & Zimmermann (Condenser Services)
October 11, 2017 • Diplomat Resort and Spa • Hollywood, Florida, USA
Project Planning
• Distortion• Misalignment• Damage• Corrosion• Erosion• Dezincification• Warpage
Tubesheetand/or Support Plate:
Anticipating Issues (Known Unknowns & Unknown Unknowns) – There are a number of common issues which can arise during a retubing that may or may not be known during the planning stages:
Kevin Squires, Sr. Project Coordinator – Day & Zimmermann (Condenser Services)
October 11, 2017 • Diplomat Resort and Spa • Hollywood, Florida, USA
Project Planning
• Connections• Baffles• Perforated Pipes• Impingement Plates / Tubing
Internal Damage:
Anticipating Issues (Known Unknowns & Unknown Unknowns) – Continued:
Kevin Squires, Sr. Project Coordinator – Day & Zimmermann (Condenser Services)
October 11, 2017 • Diplomat Resort and Spa • Hollywood, Florida, USA
Project Planning
•Ammonia Attack•Excessive Cutouts
Other Conditions:
Anticipating Issues (Known Unknowns & Unknown Unknowns) – Continued:
Kevin Squires, Sr. Project Coordinator – Day & Zimmermann (Condenser Services)
October 11, 2017 • Diplomat Resort and Spa • Hollywood, Florida, USA
Vibration and Uplift Analysis
When changing existing tube material to titanium, which is a lighter weight and generally a thinner wall thickness, the following analyses are recommended.
Uplift analysis is performed to determine if modifications are required in the anchoring areas
Vibration analysis is performed to determine whether or not the existing support plate spacing (taking into consideration the new condenser tube material) exceeds the maximum allowable spacing in accordance with HEI standards.
Kevin Squires, Sr. Project Coordinator – Day & Zimmermann (Condenser Services)
October 11, 2017 • Diplomat Resort and Spa • Hollywood, Florida, USA
Tube Vibration Resolution
Modern methods of tube vibration resolution:
• In 1978, HEI releases new edition of standards significantly expanding on the design and manufacture of steam surface condensers
• Included limitations on the allowable distance between support plates
• Specified a calculation model for predicting vibration which became the industry accepted standard for vibration calculation
• Conner’s Equation is another widely accepted model
Specific condenser configurations require stakes of different designs
Kevin Squires, Sr. Project Coordinator – Day & Zimmermann (Condenser Services)
October 11, 2017 • Diplomat Resort and Spa • Hollywood, Florida, USA
Tube Vibration ResolutionCradle‐Lock® Anti‐Vibration Tubes Stakes: If vibration or the potential for vibration is an issue, Cradle‐Lock® stakes are the industry’s standard for vibration resolution.
Patented design cradles tubes midway between support plates, locking the tubes into a vibration-free unit
Cradle-Lock® eliminates the need to rebundle when that is deemed the solution to vibration problems
Kevin Squires, Sr. Project Coordinator – Day & Zimmermann (Condenser Services)
October 11, 2017 • Diplomat Resort and Spa • Hollywood, Florida, USA
Tube Vibration Resolution
Sample Staking Plan (Modern Approach/Complex)
Detailed plan needs to be prepared showing the location of stakes
Each stake should be identified by size, style, or other parameter
Potential interferences should be considered for stake locations
Identify any areas that must be staked before tube installation can proceed
Kevin Squires, Sr. Project Coordinator – Day & Zimmermann (Condenser Services)
October 11, 2017 • Diplomat Resort and Spa • Hollywood, Florida, USA
Uplift AnalysisConsiderations
• Condensers experience an upward force due to the vacuum created in the condenser.
• It is possible that too much weight has been removed and additional restraints need to be added to ensure the condenser will not move relative to the many attachments found on most condensers.
• If on springs, adjustments are generally needed
• If on feet, additional anchors may needed
With installation of thinner and lighter tubes, analysis is required to potential effects with vacuum uplift of the condenser.
Kevin Squires, Sr. Project Coordinator – Day & Zimmermann (Condenser Services)
October 11, 2017 • Diplomat Resort and Spa • Hollywood, Florida, USA
Uplift AnalysisTypical Considerations (Sample) – In this instance, the springs will need to be decompressed by an amount equal to the difference in condenser weight.
Uplift Analysis Spring Adjustments
Aluminum Brass –17BWG
90‐10 Copper Nickel ‐20BWG
Titanium Grade 2 –22BWG
Original Compressed Spring Length
“A” Supports ‐‐‐ 18.609″“B” Supports ‐‐‐ 18.016″
Reduced Operating Weight Base 118,102 lbs 263,460 lbs
Overall Spring Rate 294,400 lbs per inch
Spring Adjustment 0 +0.401″ +0.896″
Adjusted Compressed Spring Length – “A” 18.609″ 19.01″ 19.505″
Adjusted Compressed Spring Length – “B” 18.016″ 18.417″ 18.912″
Kevin Squires, Sr. Project Coordinator – Day & Zimmermann (Condenser Services)
October 11, 2017 • Diplomat Resort and Spa • Hollywood, Florida, USA
Pullout Test
Critical to ensure optimum tube-to-tubesheet joint strength is obtained during tube expansion
Testing designed specifically for each application in order to mimic field conditions.
Customer participation is encouraged.
Kevin Squires, Sr. Project Coordinator – Day & Zimmermann (Condenser Services)
October 11, 2017 • Diplomat Resort and Spa • Hollywood, Florida, USA
Pullout Test
Test results provide valuable data such as:
How serrations affect tube pull out strength
Which torque value will provide optimal tube‐to‐tubesheet seal during tube expansion
Average wall reduction
Tube pull out strength under a range of loads
Kevin Squires, Sr. Project Coordinator – Day & Zimmermann (Condenser Services)
October 11, 2017 • Diplomat Resort and Spa • Hollywood, Florida, USA
Pullout TestPullout Test Data – Original v. Retubed Condenser – Allowable Loads
Original Condenser Retubed Condenser
Tubing
Original Basis with 90/10 CuNi Tubes,
Lmax
Tubing
Test Loads with Gr. 2 Titanium Tubes
Allowable Design Load, Lmax, lbs.
Ratio of Test Loads to
Original Basis
Ratio of Retubed Allowable Loads to Original Allowable Loads
19 BWG, 90/10 Cu/Ni
Inlet924 lbs.
22 BWG, Ti, Inlet
3036 lbs. 1263 lbs. 3.3 1.4
20 BWG, Ti, Inlet
3120 lbs. 1298 lbs. 3.0 1.6
19 BWG, 90/10 Cu/Ni
Outlet
1102 lbs.22 BWG, Ti,
Outlet2935 lbs. 1221 lbs. 2.7 1.1
20 BWG, Ti,Outlet
3032 lbs. 1261 lbs. 2.4 1.1
Kevin Squires, Sr. Project Coordinator – Day & Zimmermann (Condenser Services)
October 11, 2017 • Diplomat Resort and Spa • Hollywood, Florida, USA
Pullout Test
Summary of Recommendations – Sample
Summary of Recommendations – Main Bundle and Peripheral Tubes
Location and Gauge
Rolling Torque, in‐lbs.
Expected AWR AWR Limits Joint Strength, lbs.
22 BWG Inlets 72 23.3 % 19.3 – 27.3 % 3036
20 BWG Inlets 72 23.5 % 19.5 – 27.5 % 3120
22 BWG Outlets 75 21.4 % 17.4 – 25.4 % 2935
20 BWG Outlets 75 19.2 % 15.2 – 23.2 % 3032
Kevin Squires, Sr. Project Coordinator – Day & Zimmermann (Condenser Services)
October 11, 2017 • Diplomat Resort and Spa • Hollywood, Florida, USA
Serrating
Through the expansion process, the tube material is forced into each serration, providing additional barriers against tube‐to‐tubesheet leakage & superior pullout strength.
Installed in plain holesCan be positioned over OEM‐installed single or
double grooves
Kevin Squires, Sr. Project Coordinator – Day & Zimmermann (Condenser Services)
October 11, 2017 • Diplomat Resort and Spa • Hollywood, Florida, USA
SerratingSerrations are
created by using special cutting bits
Bits include a flat section between the 4th & 5th tooth
to ensure accuracy when measuring
benchmark holes.
Kevin Squires, Sr. Project Coordinator – Day & Zimmermann (Condenser Services)
October 11, 2017 • Diplomat Resort and Spa • Hollywood, Florida, USA
Serrating
Serrated Hole
Tube after being pushed out
Kevin Squires, Sr. Project Coordinator – Day & Zimmermann (Condenser Services)
October 11, 2017 • Diplomat Resort and Spa • Hollywood, Florida, USA
Considerations for Cathodic Protection
Cathodic protection is a technique used to control the corrosion of a metal surface by making it the cathode of an electrochemical cell. There are two common methods used today to prevent corrosion:
Galvanic System ‐ this takes the form of galvanic anodes, which are more active than the steel structure. This practice is also referred to as a sacrificial system, since the galvanic anodes—typically zinc or aluminum—sacrifice themselves to protect the structural steel from corrosion.
Impressed Current System (ICCP) - Due to the high currents involved in many seawater systems, an impressed‐current system may be used. This consists of anodes connected to a DC power source, often a transformer‐rectifier connected to AC power.
Kevin Squires, Sr. Project Coordinator – Day & Zimmermann (Condenser Services)
October 11, 2017 • Diplomat Resort and Spa • Hollywood, Florida, USA
Coating of Tubesheets and WaterboxesThe standard method of coating is to apply a thick film of epoxy coating (approximately 250 mils). Reasons to consider tubesheetcoatings may include:
Coating the waterboxes may also be done to eliminate and prevent future damage as well as for restoration purposes
Dissimilar metal combinations
Used in combination or lieu of traditional cathodic protection (sacrificial anodes)
Restore lost material due to severe damage
Kevin Squires, Sr. Project Coordinator – Day & Zimmermann (Condenser Services)
October 11, 2017 • Diplomat Resort and Spa • Hollywood, Florida, USA
Steps for Condenser Retubing
Typical Major Retubing Activities:Remove interferences
Remove waterboxes or waterbox covers (usually one end only)
Cut tubes on opposite end from “long” pulling
Remove tubes using specialty equipment; tubes are flattened and chopped into 4" to 6" piecesClean support plates and tubesheets as well as condenser internals
Serrate tubesheets (if required)
Kevin Squires, Sr. Project Coordinator – Day & Zimmermann (Condenser Services)
October 11, 2017 • Diplomat Resort and Spa • Hollywood, Florida, USA
Steps for Condenser Retubing
Typical Major Retubing Activities (Cont):
Install tubes
Stake tubes (if required)
Expand tubes
Trim, flare and/or lip tubes (as required)
Steam side hydrostatic test
Coat tubesheets and/or waterboxes (if required)
Circulating system hydrostatic test
Kevin Squires, Sr. Project Coordinator – Day & Zimmermann (Condenser Services)
October 11, 2017 • Diplomat Resort and Spa • Hollywood, Florida, USA
Waterbox Removal
Kevin Squires, Sr. Project Coordinator – Day & Zimmermann (Condenser Services)
October 11, 2017 • Diplomat Resort and Spa • Hollywood, Florida, USA
Tubesheet Array/Design
Kevin Squires, Sr. Project Coordinator – Day & Zimmermann (Condenser Services)
October 11, 2017 • Diplomat Resort and Spa • Hollywood, Florida, USA
Tube Removal
Kevin Squires, Sr. Project Coordinator – Day & Zimmermann (Condenser Services)
October 11, 2017 • Diplomat Resort and Spa • Hollywood, Florida, USA
Tube Chopper
Kevin Squires, Sr. Project Coordinator – Day & Zimmermann (Condenser Services)
October 11, 2017 • Diplomat Resort and Spa • Hollywood, Florida, USA
Tubesheet Replacement / QA Marking
Kevin Squires, Sr. Project Coordinator – Day & Zimmermann (Condenser Services)
October 11, 2017 • Diplomat Resort and Spa • Hollywood, Florida, USA
Staging New Tube Boxes
Kevin Squires, Sr. Project Coordinator – Day & Zimmermann (Condenser Services)
October 11, 2017 • Diplomat Resort and Spa • Hollywood, Florida, USA
Preparation for New Tube Installation
Kevin Squires, Sr. Project Coordinator – Day & Zimmermann (Condenser Services)
October 11, 2017 • Diplomat Resort and Spa • Hollywood, Florida, USA
New Tube Installation
Kevin Squires, Sr. Project Coordinator – Day & Zimmermann (Condenser Services)
October 11, 2017 • Diplomat Resort and Spa • Hollywood, Florida, USA
Tube Expansion
Kevin Squires, Sr. Project Coordinator – Day & Zimmermann (Condenser Services)
October 11, 2017 • Diplomat Resort and Spa • Hollywood, Florida, USA
Installation of Anti‐Vibration Tube Stakes
Kevin Squires, Sr. Project Coordinator – Day & Zimmermann (Condenser Services)
October 11, 2017 • Diplomat Resort and Spa • Hollywood, Florida, USA
Conclusion
With proper planning in advance of the project, the selection of a qualified retubing contractor, and performing the required/recommended analyses and testing, your retubing project can be completed with minimal setbacks, on time in accordance with the project schedule, and maintain budgeting forecasts.